Question on instrument calibration please?

IdealDan

Member
Join Date
May 2017
Location
MA
Posts
480
Hi Friends,


Please, I need clarification on two things:


1. I understand trimming via Zero and SPAN adjuster, BUT what MENU on Emerson 475 Field Communicator is used for Trimming?


2. For 475, Do I need to physically introduce 250-ohm Resistor on the Positive side of the the Loop? I was told that 475 has in-built 250-ohm Resistor that eliminates the need, is this true?


3. How do one differentiate between HART and FIELDBUS Transmitter?


Thanks in advance
 
1) What is trimming in Instrumentation terms?

2) Did you read the manual? The leaflet mentions this resistor as a spare part, so chances are that it isn't included and came in the box with the communicator.

3) HART runs on a 4-20mA loop and modulates digital data on top of the analog signal. A fieldbus is a digital communication protocol which will run on whatever media was defined for it... RS232, 422, 485, Ethernet, etc, etc...
 
The device model/part number is different for HART or Foundation Fieldbus.


The quick way is whether the transmitter is 4-20mA or some digital signal.


HART is 4-20mA. Digital is Foundation Fieldbus or Profibus.
 
1) What is trimming in Instrumentation terms?

2) Did you read the manual? The leaflet mentions this resistor as a spare part, so chances are that it isn't included and came in the box with the communicator.

3) HART runs on a 4-20mA loop and modulates digital data on top of the analog signal. A fieldbus is a digital communication protocol which will run on whatever media was defined for it... RS232, 422, 485, Ethernet, etc, etc...
Hi Friend,
Sorry if I'm wrong, by Trimming I mean: assuming with my calibrator I input the LRV of Psi expecting a 4mA output from the Transmitter and found out that deviates, how do I make adjustment using 475 (not 0 & span button)? What menu on 475 please?
 
There is no 'standard' menu for HART devices.


Menu navigation depends on the specific device, which is manufacturer-specific. You need the manual that covers the HART calibration method for that device.
 

Similar Topics

I have a 120V relay, 120V DI card and a analog input. I was wanting to know if i could put a 24V DI and well as a 120V DI card on the same plc...
Replies
1
Views
56
Hello again..trying something on an existing poorly written program and just wanted to double check something system is an A-B MicroLogix 1200 In...
Replies
5
Views
183
Good morning! Let me start by saying, I am still learning about this type of HMI programming. I recently watched a video about recipes and how it...
Replies
4
Views
155
I have some logic that I have written within a 5380 series controller that tracks the time an event is started, while the event is running an RTO...
Replies
2
Views
102
I have an HMI 2711R - T4T Series B, and I want to know which PLCs, besides Micro 820, can communicate with it.
Replies
2
Views
112
Back
Top Bottom