Hi,
the input current recommended is 4-20mA, but I have 34mA.
How can I bring the current parameters required.
Regards,
Ioan

5.jpg
 
Is the 34 mA moving.

Does the 34mA move and it is just high at top end? There should be a zero and span pot on the unit to set min and max output if sensor output moves and is just out of calibration. If this is in a system that has been running the sensor is probaly bad.
 
Has the transmitter ever worked properly or are you trying to get it running the first time?

If it worked before and now outputs 34mA, then it is not regulating the loop current as it should. That's it's job, to regulate the loop current to a maximum of 20mA. If it doesn't do that, there is 99% probability that it is broken and that you need to replace it.

There is 1% probability that a ground loop has been created which adds current to the loop. That could be something like a loop wire with frayed (missing) insulation that touches an ungrounded motor with a winding touching the frame and the differing potentials puts current into the loop. Or water in a junction box, but injection molders typically do not have junction b boxes out in the weather.

The test is to substitute a 4-20mA source (calibrator) and see if the loop current is the same as the calibrator is sourcing.
 
Yes machine worked before, but I had to change the way 1746- NIO4V and then I noticed and value of 34mA.
sensor model is 2200BG C2501A3UA (Gems sensor)
A pressure can lead to 34mA value?
 
Last edited:
The inputs on your card can be configured for voltage or current operation. Have you set the card up properly?

If you disconnect the wires from the card and just connect them to a meter in current measurement mode, what do you read? If this reading is over 20mA then you sensor almost certainly damaged as Dan suggested.
 
It looks like it has 2 outputs connected.
the relais must be in!
btw bad practice to have a 20 mA switched by relais,however it can work.
 
Looks, you have voltages drop, you are not getting 24 volts (Suppose). There is no scaling between 4-34 MA.
 
in the attached image shows a potentiometer (POT 10K).
Can someone tell me what values adjusts the potentiometer?
Regards
 

Similar Topics

I have a 120V relay, 120V DI card and a analog input. I was wanting to know if i could put a 24V DI and well as a 120V DI card on the same plc...
Replies
1
Views
60
Hello again..trying something on an existing poorly written program and just wanted to double check something system is an A-B MicroLogix 1200 In...
Replies
5
Views
184
Good morning! Let me start by saying, I am still learning about this type of HMI programming. I recently watched a video about recipes and how it...
Replies
4
Views
160
I have some logic that I have written within a 5380 series controller that tracks the time an event is started, while the event is running an RTO...
Replies
2
Views
102
I have an HMI 2711R - T4T Series B, and I want to know which PLCs, besides Micro 820, can communicate with it.
Replies
2
Views
112
Back
Top Bottom