Hello all,
I have some doubts regarding the sizing of the protection and cables for a reactive compensation.
The reactive I have to compense is 100Kvar, for which im planning to put 4 capacitors of 25kvar each.
For each capacitor i will put special contactor por capacitors rated for 25kvar and a thermomagnetic circuit breaker of (25000/(400*1.73))*1.5=54A
As I have read in many articles, the breaker should be sized 1.5 the nominal current of the capacitor. The cable will be of 6mm2.
all 4 circuit breakers of the capacitors will be feed of a breaker sized (54*4)=216A and will use a infeed cable of 50mm2. The main circuit breaker is it necesary to be sized *1.5 of all nominal current ??
Is all this correct ?? make sense ??
Thanks!
hi.. i have a reactive power meter..i would like to visible in my HMI.the hmi has built in analog input module..that allow different input...
1,154
Hello all, I am currently trying to program a PowerFlex 525, version 7.0. We had a power outage recently and when the power was restored, the...
197
Looking at installing point io, with a 1734-AENTR communications adapter and ten 1734-IT2L modules. In IAB it installs a 1734-EP24DC after every...
51
First time I've used either the software or this unit. This is the setup I have right now. I have 20mA coming into AnalogIP1. Both the Main.PV...
43
Hello..I am new to Plc.I have Mitsubishi Melsec Fx3Ga-40MR PLC controlling a machine for packing powder.Currently the Plc has issue which power...
143