Read string from DB to FB
SeH
Jun 2011
Göteborg
I'm having a problem again. This time I'm trying to read a string from a DB and compare it to a string given by an input variable in the FB. The problem seems to be when reading the string from the DB. It should be a string containing '0', '1' or '2' but in the FB it is a dword containing F013100. Here is some of the code:
Code:
FUNCTION_BLOCK  Recept_hantering
    // *** Variable declarations ***
    //Temporary variables
    VAR_TEMP
        loopnumber : INT;
        i : INT;
        temp_article_nr : STRING[15];
    END_VAR
    //Static variables
    VAR
        area_start : INT;
        editable_start : INT;
        active_start : INT := 0;
    END_VAR
    //Input parameters
    VAR_INPUT
        load : BOOL;
        save : BOOL;
        activate : BOOL;
        recipe : BLOCK_DB;
        article_or_position : BOOL;
        sum_articles : INT;
        article_datalength : INT;
    END_VAR
    // *** Program start ***
    BEGIN
    loopnumber := sum_articles;
    editable_start := article_datalength;
    temp_article_nr := '';
    temp_article_nr := article_nr;
        area_start := article_datalength;
        i := 0;
        //Check for model with matching article number
        REPEAT
            i := i + 1;
        UNTIL temp_article_nr = DINT_TO_STRING(DWORD_TO_DINT(recipe.DD[area_start + article_datalength * i])) OR i > (loopnumber - 1) END_REPEAT;
END_FUNCTION_BLOCK
The string is stored in the following format:
Max string length, actual string lenth, char 1....etc,
This ties up with your data: 0f, 01, 31, 00 (Note that '1' is 31hex). You have to copy the bytes from the DB to the destination string, not convert the dword to a dint then convert the dint to a string.
Example code (compiled but not tested - supply the DB and the call to the block next time. Create a library and copy the blocks the library, archive the library and then post as an attachment.)
Code:
FUNCTION_BLOCK  FB998
    VAR_TEMP
        loopnumber : INT;
        i,j : INT;
        sFromDB:STRING[15];
        byFromDB AT sFromDB: ARRAY[1..17] OF BYTE;
    END_VAR
    //Static variables
    VAR
        area_start : INT;
    END_VAR
    //Input parameters
    VAR_INPUT
        load : BOOL;
        save : BOOL;
        activate : BOOL;
        recipe : BLOCK_DB;
        sum_articles : INT;
    END_VAR
    BEGIN
        i := 0;
        REPEAT
            i := i + 1;
            //copy string from db a byte at a time into temp string variable
            FOR j:=0 TO 16 DO
             byFromDB[j]:=recipe.DB[area_start + (article_datalength *i) + j];
            END_FOR;
        UNTIL temp_article_nr = sFromDB OR i > (loopnumber - 1) END_REPEAT;
END_FUNCTION_BLOCK
Now it seems a bit more promising but it still doesn't work. I've added the DB and the block call and also the code in an attachment (I hope it works). When I debug the program I find that byFromDB[0] = 0F , byFromDB[1] = 01 , byFromDB[2] = 31 and the rest is 0. So far so good. But it seems like sFromDB is 0 or empty. Do you have any idea why?
Another question: is it in any way possible to see the value of a string online?
My coding error. Array should be [0..16] and not [1..17]
Code:
        byFromDB AT sFromDB: ARRAY[0..16] OF BYTE;