Reading and writing Minutes and seconds in TIA Portal?
asteroide
Jul 2010
der
158
Hello Friends
My experience with Siemens is limited.
From HMI I would like introduce Minutes and Seconds to a timer.
Also, in HMI I would like to show the time of the timer in minutes and seconds.
I have achieved only to show in accumulated seconds.
How can I do what I want?
Thanks in advance.
To extract h/m/s from TIME You could do something like this.
Code:
FUNCTION "fcTimerRemainM" : Void
{ S7_Optimized_Access := 'TRUE' }
VERSION : 0.1
   VAR_OUTPUT
      udiHours : UDInt;   // Hours left
      usMins : USInt;   // Minutes left
      usSecs : USInt;   // Seconds left
   END_VAR
   VAR_IN_OUT
      tTimer {InstructionName := 'TON_TIME'; LibVersion := '1.0'} : TON_TIME;   // Timer data
   END_VAR
   VAR_TEMP
      udiDiffSec : UDInt;   // Time difference in seconds
   END_VAR
BEGIN
	    fcTimerRemainM
	    This function is used to display remaining time of running timer.
	    Function provides cumulative hours, minutes and seconds.
	#udiDiffSec := TIME_TO_UDINT(#tTimer.PT - #tTimer.ET) / 1000;   // -- Get difference between Set - Passed time in seconds
	#udiHours := #udiDiffSec / 3600;                                // -- Get hours left
	#usMins := UDINT_TO_USINT(#udiDiffSec / 60 - 60 * #udiHours);   // -- Get minutes left
	#usSecs := UDINT_TO_USINT(#udiDiffSec MOD 60);                  // -- Get seconds
END_FUNCTION
Is it possible that initial divide by 3600, to calculate #udiHours, will round (e.g. 1801s becomes 1h)? If so, the following will work:
Code:
// -- Get total seconds, place in hours variable for now
// -- N.B. we don't care if the divide-by-1000 rounds to nearest second
#udiHours := TIME_TO_UDINT(#tTimer.PT - #tTimer.ET) / 1000;
#usSecs := UDINT_TO_USINT(#udiHours MOD 60);   // -- Extract seconds of minute
#udiHours := (#udiHours - #usSecs) / 60;       // -- Convert balance to Minutes
#usMins := UDINT_TO_USINT(#udiHours MOD 60);   // -- Extract minute of hour
#udiHours := (#udiHours - #usMins) / 60;       // -- Convert balance to hours
Thanks for your help.
My main experience is with ladder, so I have done in ladder and it s working for showing time.
In my program I need to use around 30 timers and show in minutes and seconds in hmi, so I need several tags to convert to minutes and seconds.
How do you recommend to assign the timers and auxiliar registers?
1 DB for timer and its auxiliar registers o how can I do that?
Thanks again
You just need to make a function, for example the one which is included in this thread.
If You don't know how to import a source in tia look here:
https://support.industry.siemens.com/cs/document/79168964/how-do-you-import-blocks-in-a-step-7-(tia-portal)-project-that-were-created-in-other-projects-or-with-earlier-versions-of-step-7-?dti=0&lc=en-US
Because of Your question it seems, that You are not familiar with Siemens Plcs, I would recommend reading this manual, especially chapter Code reusability, which will be good introduction on functions.
https://cache.industry.siemens.com/dl/files/084/109478084/att_900353/v1/81318674_Programming_Styleguide_DOC_v12_en.pdf
Summary: How to remotely toggle BOOL values on a vendor-supplied system having a L24ER PLC? (RSLogix Studio 5000 version 33.01.00) I have a...
1,710
I am reading and writing to I/O tags in Logix5571 using python. While dissecting using Wireshark, I could see that the Symbol Class(0x6b) is being...
1,332
Hi again guys, This forum has been great for all the questions ive asked these last few days. Another one now.. haha I am currently working...
4,207
Hey guys, i'm controlling altivar 71 drive from modicon m340 cpu 2020 plc through modbus communication, when I read and write at the same time...
2,208
I am new to this. I have a customer wanting to use a MicroLogix 1400 to control a Mitsubishi A8NEIP-2P. All I can find on the Mitsubishi site is...
2,237