Previously you wrote
To sum it up:
According to your last diagram, with the common being the "bottom" of the voltage splitter, you can hook up your 0-10V datalogger input to the "middle" and your 24V PLC input to the "top" of the voltage splitter. Power supply, datalogger input channel and PLC input channel must share the same common.
In an industrial application, this would have been done with a signal conditioning isolation amplifier, not a voltage splitter. But in principle there should be nothing wrong with doing it this way.
That more or less prompts me to verify that you circuit is OK. The point is that in order to figure out if yor circuit is OK or not, I have to know the details. It shouldnt be necessary to d.r.a.g them out of you.Jelf said:If I understood correctly, that shouldn't be problem?
To sum it up:
According to your last diagram, with the common being the "bottom" of the voltage splitter, you can hook up your 0-10V datalogger input to the "middle" and your 24V PLC input to the "top" of the voltage splitter. Power supply, datalogger input channel and PLC input channel must share the same common.
In an industrial application, this would have been done with a signal conditioning isolation amplifier, not a voltage splitter. But in principle there should be nothing wrong with doing it this way.