Hey Guys,
I was needing some advise on what
device you would recommend using
to read/monitor oil Level from a horizontal
tank?
In normal operation this oil tank would
Only be half full max.
scale of tank at half oil level would = 100%
I would like to have a device that would
Provide a 4-20 mA signal.
In your guys past experience
Is there a device that would be durable
To the elements of oil but still monitor
Oil level?
Thanks for helping
There are a lot of different level transmitter that we use in the Oil industry. For a non-contact type of transmitter Emerson makes a good radar gauge.
If you want a float type of transmitter Varec makes a very good float and tape gauge that you can add a transmitter too.
There are many different ways to go here. You budget and accuracy requirements will determine what you end up with.
I would also caution against getting a tank gauge that only covers half the tanks level. That is a good way to have a spill!! Get one that covers the total range of the tank. Even if they only plan on using 50% of it. That always changes in my experience. Do it right the first time and then you never have to worry!!
If you can provide the tank dims and a idea of your budget and accuracy required I may be able to get you some more options.
As Bullzi says your budget and accuracy will play a big part. We are getting ready to install a Rosemount 2501, it will be installed such, that a pipe will be plumbed into the tank with the bottom open.
A rise or fall in the level will change the pressure in the pipe
As a safety we are installing a float for maximum shut off if it occurs.
https://www.instrumart.com/products/24683/rosemount-2051t-pressure-transmitter
Hey Guys,
tank?
Oil level?
Thanks for helping
What about a Pressure transducer? use it as hydrostatic level Transmitter. Ultrasonic transmitter might also be a good instrument
I need help with vijeo citect 7.4 as I use Modbus TCPIP to get the data, it turns out the address is having error.. For example, when I write...
889
147
Hi all, i have 8 CJ2m plc units that show different numbers on the plc display and i am stuck on reading the info. my unit has an ip address of...
102
Hi Everyone, I am not proficient in RSLogix 500 so I have a question regarding the evaluation of N7:0 data as an input. So as I understand in...
87
Trying to setup a message read via Ethernet. I have the path setup as 1, 1, 2, 192.168.66.10 I get an error code 1, ext err 315. I am beating...
233