Hi all,
I am looking for someone that as some knowledge setting up a Redlion Data Station plus.
I am looking to read a number of registers from a AB Controllogix PLC and forward the registers to a Unitronics PLC via Modbus TCP/IP.
At the minute the PLC is connected to a scada computer running RSview via a Ethernet hub.
What I'm wanting to know is:
1) Will the redlion convert Ethernet/IP to modbus TCP/IP so that I can read the registers on the Unitronics PLC?
2) Will communications work if I connect the redlion, controllogix & Unitronics plc to the Ethernet hub and assisgn different IP address for each unit?
Hope someone can point me in the right direction!!
Yes and yes.
Tell us about the addresses you need to link together and we can help you set up "gateway blocks" to make the data flow between the two plcs.
If you are interested, I can give you a free application that can run on your SCADA computer, read tags from the ControlLogix and transfer the values to Modbus registers. It will do what you want without having to add more hardware.
I seem to remember a sample PLC program that would let you write directly from the ladder code to a Modbus device, but I am not sure if it was for the ControlLogix series or the MicroLogix series. I am not able to find the web page with the sample program. If it is possible, this would be the ideal solution.
UPDATE: I did find some information on using Modbus directly in ladder code:
http://theautomationblog.com/which-controllogix-models-support-modbus/
The link to the ModbusTCP example is still valid and free to download the sample program.
Hey Archie,
Got your PM. Thanks for your input.
All the ports on the ControlLogix are used up. All I can use is ethernet.
Thats great OkiePC, I have roughly 20 floating point values that I need to read from the controlLogix and send to a Unitronics v570.
I have created a .L5k file to reference the tags.
If your Logix PLC has firmware v20 or higher and on the same Ethernet network as your other controller, I would try the Rockwell ModbusTCP Master solution first. With no "middle man" hardware, it will be the most reliable solution.
Can anyone help me getting this comms connection set up? I am using Port 2 on the Versamax ICU200UDR005-DK, set in SNP with port settings Baud...
1,560
Hi, I've been told to get the Red Lion Data Station to an Allen Bradley Compact Logix L32E. I want just basic comms established between the two...
3,484
Hi, I'm currently trying to connect a Redlion DSPSX to a Siemens S200 PLC. I can ping the S200 PLC and the DSP but I cannot get the two to talk...
4,430
I am polling 16 bit Integers from a Horner PLC and things work fine. I need 2 32 bit floats from the same device but I can't seem to get the right...
3,322
Hi, I have a complex database in Crimson 3.0 and in one of the display pages I am trying to get a tag to show the sum of several other tags. The...
173