Redundant PLC
pejo
Jan 2008
Stabroek
Due a reorganization in the company we want to work with a redundant system. We have to couple with RS232/RS485 systems. I only worked with Siemens until now, but I assume that there are also other systems on the market. What are the most frequented used systems for the moment (Siemens,Phoenix, AB,….), what is the experience with the systems?
Hello,
We use redundancy often in our projects. We used following solutions:
- Siemens
- Telemecanic
- Phoeninx contact (only studied)
In my experience the siemens redundancy solution S7 400-H not the 300 redundancy is the most flexible and easiest to configure. You program both cpu's as one cpu. And you can access the data from both cpu's in both cpu's.
As for pricing, the siemens solution is one of the more expensive solutions.
In the end you will have to consider what the requirements are for your specific solution, and witch solution to implement.
Regards,
Marsupilami
Hi guys, Just wondering if anyone has tackled an issue similar to this before: creating a redundant master on Modbus so I can have a redundant...
448
Good morning to all, I need to modify PLC configuration adding a new Profibus card. I've an issue during upload of actual configuration. With my...
600
Hi sir. We are using Control logix redundant PLC system which supports only PTP time synchronization protocol but from DCS side we are receiving...
2,432
Dears ALL I am preparing new PLC panel I want from the contractor to make redundant CPU , power supply and I/O modules, the contractor refuse to...
3,077
Dear all, I have a problem with the Mitsubishi PLC modbus tcp communication. I'm using a L26CPU and LJ71E71-100 ethernet module to perform a...
3,939