Relays?
Ken
Jul 2002
43
Hi guys. been searching the net for a while regarding relays. hope you guys can help me with it. I'm actually looking into the possibility of replacing all the electromechanical relays (OMRON MY2J) with solid state relays. Is there any direct pin to pin plug and play type of solid state relay that i can get my hands on?
regards
Ken
I do not know of any type of Solid State Relay which will plug into your relay socket. Also Solid State Relays are single pole, normally open contact which may not be suitable for your application. Are the relays used to switch loads or are they used in a logic application?
IDEC makes a solid state relay (type RAPP) that uses the same 8 pin tubular socket as their standard relay. It looks like the wiring is identical for the NO contacts.
Thanks. will go check them out. Omron G3F series is also using the same pin out and mounting terminal but i'm wondering if i can just replace the electromagnetic relay just by changing them. Any ideas?
Ken:
If you are switching a DC load, you will have to make sure that the load polarity is right - unlike the contacts of a mechanical relay where it doesn't matter. A solid-state relay is, in essence, an SCR (a.k.a. a "thyristor"). Think of it as a diode that can be switched on or off. It goes without saying that a diode conducts only in one direction.
On the same token, if you are to switch an AC load, you must use an AC SSR, which is a combination of two SCRs, connected in parralel in opposite polarity. Of course, all this a simplification - there is more in industrial SSR than just one or two SCRs. But it describes its behavoir pretty well.
One other inherent property of an SSR is that the load current should not be too low, otherwise it will never switch on. This information may be found in manufacturer's datasheets. Another difference is that, like all the solid-state components, it doesn't handle overcurrents well and tends to break down first, before any fuses would blow. The failure of an SSR would invariably mean that your load will stay energized all the time; think about potential dangers for your application if this ever happens (and it will, sooner or later ;) ).
Make sure that your load inductance and capacitance do not exceed the SSR specifications, since SSRs are much more "picky" about any kind of transient effects. They work much better with purely resistive loads.
Generally, I would use an SSR for a fast-switching load, or a pulsing one - a heater is a classical application. Don't forget that an SSR is typically more expensive than a mechanical relay of the same load capacity. There must be a good justification to replace everything at once.
Hi all, looking to model old RR relays in PLC. Does anyone have any SPECIFIC examples on how to model a relay such as a polar relay, slow pickup...
82
I tried the click plus PLC to send emails today but could not get it to work over my network. I need a mass alert when a temperature reaches a...
421
Hey guys, the scenario is: I have already completed the drawing package for my system utilizing an A-B 440R-N23126 (Minotaur) safety relay. SoS...
165
I'd like to talk this through a little: Relays are regularly used for PLC outputs, regardless of a need for signal conversion. But what about...
963
Good Evening , I should know more about Solid State Relays . I have a system with 8) 120 vac Vibrators . These Solid State Relays have...
24
2,109