Remote I/O

Jezz

Member
Join Date
Dec 2002
Location
Kendal
Posts
399
Hi all,
The boss has finally given me permission to get rid of the PLC 2 :D :D :D and replace it with an RIO Adaptor and a RIO scanner in a nearby SLC 5/03 do I need a special cable to connect these two?

Does any one have any usefull links befor I start..


Thanks Jezz
(y)
 
As far as cabling, just the ordinary "blue hose" (usually Belden 9463) will do. When you purchase the scanner card for the 5/03, there should be terminating resistors with it that need to be installed at the physical ends of the network. For more information about the scanner card, see:

http://www.ab.com/manuals/io/1747/1747-in060d-en-p.pdf

Also, search the AB site for articles on block transfers. You will need how to program them in the 5/03 to address your non-binary data.

Good Luck,
Jeff
 
It's all binary at the moment we may add analog later but I might just put that in the 5/03 instead of on the RIO..

Jezz
 
Hi,
I've started reading the manual and it mentions using the Advanced programming software to configure the system can some one explain what APS is we have RS Logix 500 on site but I'm not sure about APS???


Jezz

I Think I've just found out how to do it in the I/O config right click on the scanner then Adv config .....

Am I right
 
Last edited:
APS is the old DOS programming software for the AB PLC's. There may still be a few copies in use out there, although I don't believe AB supports it anymore. You will be able to do everything you need to in RSLogix by going to the IO Configuration tab, highlighting the Scanner card, and clicking Advanced Configuration. This is where you will set up your G-Files, M file length, and do your remote rack configuration. This will make more sense when you have an actual scanner to play with.

Jeff

Oops..sorry....didn't see the last part of your post. It sounds like you're on the right track :)
 

Similar Topics

Something I've never thought about before... maybe you folks have some thoughts or experience. I have a customer that uses a Weidmuller, Modbus...
Replies
2
Views
51
Hi, We have been facing a issue with SCADAPack 474. Configuration is like below. RTU 474 + 6103 PS + 5606 IO Mix Module + 5414 DI Module Only...
Replies
0
Views
72
Hello, Can anyone recommend an expandible IO module with OPC UA? I've deployed the Emerson RSTIO-OM module and it works great, but it has a...
Replies
0
Views
53
So I'm pretty new around here but I come looking for advice or suggestions to research. Im the plant electrician/SCADA guy for a warer department...
Replies
8
Views
290
See the screenshot of EIP tag list. We are trying to read in a digital input that is hard-wired. It is shown here as I31.1. I believe we cannot...
Replies
7
Views
306
Back
Top Bottom