I just recently installed a1771 HSCM in a plc 530 and for the life of me I cannot get the reset fuction to work. all the Numbers in the encoder card seem to be hard coded and cannot be changed by toggleing the reset bit. Also I cannot load the preset vaulues by toggling that bii either. The block transfer reaed and write box instructions see to be working perrectly but I cannot overwrite the hardcoded numbere that reside in th encoder. The book seeems very straight foreward but it does not work. When I toggle these bits it just checks the 2 boxrs in the setup screen. Could someone please tell me what I am doing wrong. All I want is a soft reset and a soft preset load when the corresponding bits are checked
Thank You so Much for your Help
Tommy Thompson
Hmmm. is is possible you typo'd the catalog number?
1771-VHSC is a valid part number...
I haven't dealt with that module in over ten years, so I doubt I can help, unless you could post your code.
Response
You are right the part number is a 1771-VHSC As far as the code I am using 2 rungs of ladder one for the BTR and the other for th BTW and then setting the corresponging bit to reset the counter and then load a preset. It is ver simpel bur the bits do not do what they are suppose to do. I also realize that the plc5 are aincent and the Control Logics are now the thing of the present. Thanks for your reply
Tommy
I would get a copy of the user manual for the 1771-VHSC. You can find it here:
http://literature.rockwellautomation.com/intradoc-cgi/nph-idc_cgi.exe?IdcService=GET_SEARCH_RESULTS&QueryText=%28dWebExtension+%3CMATCHES%3E+%27pdf%27+%3Cand%3E+%28%3Cnot%3E+xViewableFile+%3CMATCHES%3E+%27No%27+%3Cor%3E+xViewableFile+%3CMATCHES%3E+%27%27%29+%3Cand%3E+%3Cnot%3E+xReleaseToFlag+%3CMATCHES%3E+%27Restricted%27+%3Cand%3E+dSecurityGroup+%3CMATCHES%3E+%27Literature%27+%3Cand%3E+%3Cnot%3E+xBrand+%3CMATCHES%3E+%27Other%27%29+%3CAND%3E+xCatalog_Numbers+%3CSUBSTRING%3E+%601771-VHSC%60+%3CAND%3E+%28xLanguage+%3CSUBSTRING%3E+%60EN+-+English%60+%3COR%3E+xLanguage+%3CSUBSTRING%3E+%60MU+-+Multi+Lingual%60%29&DefaultQuery=&urlTemplate=%2Fidc%2Fgroups%2Fpublic%2Fdocuments%2Fwebassets%2Fsearch_results.hcst&ftx=&SortField=dDocTitle&SortOrder=Asc&SortSpec=&passedLangVal=EN+-+English&prepopVal=1771-VHSC&passedType=xCatalog_Numbers&passedParameter=1771-VHSC
These RESET functions from the User Manual seem to be relevant. Notice that you must do a BTW to reset the count.
Software Reset
The counters can also be reset by the Reset Count bits found in Word
1, bits 0-3 of the block transfer write. When one of these bits is set
to 1, the associated counter is reset to zero and begins counting. The
module can also be reset with the gate/reset as explained below.
Refer to chapter 4 for further details.
Gate/Reset Input
There is one gate/reset input for each of the 4 counters. The
gate/reset input, when active, will function in one of the 4 store count
modes outlined below.
Hello, I still do not have equipment in to test. But the RTAC ladder does not have a timer reset coil. I wonder if a reset coil on Timer.IN is...
124
Hi, i am using DVP-14SS2 PLC, after program written to plc, when power is reset, plc doesn't run. always need to connect to pc for the run mode.
62
Hi need help why this “failure 5 emergency stop “ appears at every startup in the morning ? Have to shut off main switch at least 10 times on...
19
401
I was loading a program onto an XE1e2 PLC and it got stuck on these two windows and won't progress. It won't let me connect from the PC to reload...
101
Hi all, i have recieved some 4RF Aprisa SR+ ethernet radios from a customer to configure. Issue is that they are used and have non-default...
110