Retrieving data from PM800 via Ethernet Gateway EGX
hcahyadi
Dec 2004
Hello world!
I am trying to grab data from Power Meter 800 via Ethernet Gateway EGX400. I have followed the manual and try to read the volatages from the power meter. And when it comes to see the data from the register (via Concept 2.6), it displays 0 at all time. Can anyone who knows how to setup such case share their experiences please? I might be missing something.
Thank you very much,
Harry
Harry,
I am not familar with "Power Meter 800". Is that a power monitoring interface similar to the Square-D POWERLOGIC circuit monitor? If so, the most likely cause of non-performance is not successfuly establishing communications between the Power Meter and your computer.
How can you check to be sure that the Power Meter is sending data to your Ethernet network? How can you check to be sure that your computer is receiving data from the Ethernet network? You may need another monitoring program to determine if you have communications or not.
Dear Lancie1,
Thank you for the reply. I have just solved the problem.
Yes, it was indeed due to non-performing communication between the EGX and the PLC.
I tested the EGX using a communication tester directly from the PC, and it was able to read the values of PM800 via the EGX.
I configured the I/O scanner in Concept to retrieve the values via PLC.
Now that the problem has been solved, I would like to close this discussion.
Thanks again,
-Harry
Hi, I cannot find the DLCA1764.EXE utilty software for data retrieving. Can someone share the link to download this software. Thanks!
133
I have a strain gauge attached to a load cell. The strain gauge is wired into an analog channel on a ControlLogix 1769 controller at +/-10V. How...
2,431
Hello to all, this is my first post, but many times I had found help on this helpful forum! Currently I'm using a PTV from Red Lion controls...
6,339
So I've finally been able to manage to get the ip address set, and I've got connectivity via tcpip, as well as connectivity via rslinx classic...
19
4,453
I have a few remote locations that are relay logic panels. I would like to monitor the panel with an AB micro 1100 and a small panel view. I would...
5,676