RFH -> Cooling -> avoiding fire and failure

MASEngr

Member
Join Date
Nov 2007
Posts
79
I have a new PLC system that requires a fair bit of cooling. All the components dissipate 170W, worst case. (one hundred seventy watts) There's a DL-06, a few VFDs, and 4 5W safety controllers.

Here's where it gets tricky:
1. The cooling system has to be NEMA4 / IP66, since we're near the ocean.
2. There's no compressed air available, so vortex is out.
3. The cooling has to be small. The width can't be more than 6".
4. The outdoor temperature is up to 40C. (Heh, I can't use the word formed by amb + ient)
5. The components will start failing at 55C, so a limit of 50C is required.
6. The system is outdoors.
7. The system will be moving, so water cooling is out.

Some easy bits:
1. There's a large aluminum plate that can be used to remove a small amount of heat. (5' x 3')
2. There's a large plate on the front as well, although the users may be touching it, and it might get hot in the sun.

What in the world can I order that will let me cool this system off?

Thank you.
 
Last edited:
Is this that ramp? Most ramps I have seen have one end tied to shore and other (moving end) connected to ship.
Why cant you use flexible hose to supply water to the cabinet then use readiators inside to cool components? What is sea water temp at the dock. Or braze solder whatever tubing to backwall of cabinet on the exteriorer (yeah I know I cant spell that XXXX word) to prevent leak damage??

You could use dry ice, liquid nitrogen OR
a small hermetic heat pump.
When you do this look in ASHRAE for relative humidity and dew point values to prevent condensation problems.

If you do not shade it (forget might - it WILL get hot in the sun) then I think you should consider solar radiation contribution to your total heat load.

Dan Bentler
 
Yes, this is "that ramp" - thanks for remembering. It's still in progress. The PLC code is done, the electronics have been designed, parts are on order, and RFQs are out for the custom components, like the enclosure and the power track. We're planning to have it installed by the end of the summer. It's quite exciting.

The ramp is between the pier and the floats on a jetty, and the carriage is moving between the two points. At present, the design is to house the electronics inside the carriage - that means I've got just two mains lines, one RS-485 line (4 wires in one bundle), and 2 estops in the moving parts. If I house the electronics on shore, I'm looking at more than 40 x 16AWG lines plus other problems.

There is an awning over the system, so it won't get lots of direct sunlight.

I guess I could run a cold water line in the same track as the power, but I've spent a lot of time and money keeping water OUT. ;) Before I did that, I'd get a big honking compressor and run a vortex cooler. (Which I thought were perfect until I saw the amazingly large air requirements!)
 

Similar Topics

I need to protect some pressure transmitters from hot (120°C) oil. Does anyone have a favorite transmitter cooling element/standoff they use...
Replies
4
Views
180
Do you know a supplier for the following item? Similar parts and other brands are acceptable. cooling fan for servomotor mounting Rexroth...
Replies
2
Views
1,375
Hi; We are working for selection of a rotary cut-off for our corrugator machine and getting quotations of different companies. A USA company...
Replies
0
Views
1,725
I have to build a new cabinet to house a 22-inch touch screen, Mini PC, Panel Mount UPS, Ethernet Switch. It will be in an area that is extremely...
Replies
7
Views
3,251
Hello, I got a customer that has a shrink wrap machine to bundle up beer cans to make beer packs. They have a problem with the oven's all metal...
Replies
10
Views
4,342
Back
Top Bottom