I have a Panelview 550 that I am converting to a Panelview Plus 700 with a Rslogix5 plc, the communication is with RIO. I have never done a setup for this before. I have already converted the program from Panelbuilder 32 to Factorytalk view studio. I am having an issue trying to set up the communication for the new PV. I believe that I have to set up the block transfers, in PB the address are set as N but in FT they are B, do i have to switch things?
Welcome to the PLCTalk forum community !
Unfortunately you've chosen an old and clumsy conversion for your first post. I was one of the experts on this syntax and troubleshooting... 19 years ago.
Let's take a step back: the PV+ needs a RIO adapter, which was the 2711P-RN6 daughtercard for the old pre-PV+6 hardware. The PV+6 and 7 hardware doesn't support those daughtercards.
What hardware and firmware on the PV+ terminal will you be running ?
Examine your PLC-5 program and document exactly which Input and Output data elements are assigned to the PanelView Standard, and which N-files are used by BTR and BTW instructions in your PLC-5 program.
"N" and "B" files are essentially the same in PLC-5, they're both 16-bit flat data files. The principal difference is in whether your consider them bit-by-bit or as a whole 16-bit signed integer.
Where do you see "the N files are shown as B files" difference ?
Screenshots that are scaled, trimmed, saved as PNG and attached to posts are a great way to share that sort of information with the Forum.
And again, welcome !
Ken,
If the daughter cards are not available for newer hardware, I have used a Prosoft conversion module that connects to a PVP+6 over Ethernet. I want to say it was RIO to Ethernet but it may have been DH+.
FWIW, the setup was fairly straight forward and it has a web server interface where you setup the comms.
If the OP is unable to find a solution, I can post the specifics of the module I used in the AM.
Unfortunately I didn't have a choice in this project, the equipment here is well over due for an upgrade. But the PV+ 700 I was told to use does have a 2711P-RN6 card attached to it, again this is what my boss told me to use. I attached two pictures one of the existing PB32 comm setup and one of the FT I was building and tying to set up per what i have found on the web to do. Any help would be greatful.
I've been searching the forums for hours and I've found many things to try but just haven't found the right answer yet. I have a running PLC 5...
1,868
Hi,I'm trying to migrate only CPU from PLC-5 to CLX and I/O modules are still PLC-5 series. I think, the migration works is almost done but I...
1,727
Hey Guys, We had one of our guys try to modify a program on a loader here, he didnt upload before the download........... No we have a flashing...
2,041
Hi everyone! I'm doing a upgrade here at the company. I`m replacing the Panelview 1400e to an 1500 plus. I`ve already made the tests on my pc by...
4,111
Hi Master Sifu, We have plan to upgrade our SLC to CLX controller while remain the PanelView communication. I have a panelview plus 1000 with a...
2,675