Rockwell/Controllogix In-Chassis OPC UA Server
pegla00
Jul 2015
Toronto
Hi All,
Has anybody had any experience with this module - Softing OPC UA Server Controllogix module (setup, operation, etc.)?
For this new project I would rather have hardware based OPC UA server.
Thank you.
We've used them a few times. I didn't get a chance to use it myself, but from what I was told, setup and operation was pretty straightforward.
OG
I've not used that specific module, but I've used their in-chassis SQL bridge module and found it to be very straightforward and user friendly.
Hi All,
Thank you.
I know this product very well and I can recommend it.
Code:
The module spec says there is a maximum of 1000 tags - any issues with that?
Are UDTs allowed, if yes how is the tag count then calculated?
Thank you.
According to the technical details in the website, UDTs are supported:
  • OPC UA Client compatibility for scalar tags, UDT component tags, and arrays
  • Complex Type Facet ControlLogix UDT Support (6.5.11)
https://data-intelligence.softing.c...les/eatm-opc-ua-server/#tx-dftabs-tabContent1
I cannot find the statement you mention with regards to a limitation of 1000 tags. I am not aware of such limitation. Can you please point out the document you have seen with this information?
You are both right, there seems to be no limit to the number of tags, the site says transmission speed up to 1000 tags/sec.
Thank you.
Ran across this, could be trick or it could be real... not sure but they also have a Schneider example...
7,483
We have an OPC Server for our Proprietary DCS which is currently communicating (bi-directionally) with a Wonderware front-end, but I'd like to use...
2,300
Need help. We have a plc that's cpu keeps getting maxed out. We've already upgraded it once. Now we need work on optimize it. We have over 50...
3,055
First of all, my thanks to the following members who tolerated my recent bellyaching about the scaling of input values in the thread "ControlLogix...
21
6,565
Hello all, A customer is replacing some equipment, and in this process a server utilising TCP/IP protocol will need to communicate with an...
1,839