RS 485 communication problem

Himanshu

Member
Join Date
Oct 2023
Location
Gurgaon
Posts
2
I am having PLC S7 200 smart model- ST 30 .
In which I am getting problem in modbus communication of PLC and VFD via built in RS 485 port of PLC.
PLC is not able to communicate also PLC RS 485 port is heating during communication. What could be the possible reason of this problem and what can I do?
 
Hi and welcome to the group. In serial communication whenever things do not work I recommend reviewing the basics. Check the cable and pin assignment for both interfaces and confirm correct cabling. Also, if there is no termination you should add it. It may have worked in the past without termination in marginal conditions, but whatever changes in the setup you are experiencing communications may not work without termination. Also, check whether the baud rate settings were changed.
 
RS 485 problem

ok i will try it. Actually i was not using termination because i have another plc ST20 which is communicating properly.
but sure i will try it.
 

Similar Topics

Hi.. I am using Micrologix 1400 PLC & C600 HMI. I want to do the communication between them by DH-485 via RS485 port.( As distance between them...
Replies
2
Views
4,296
Hi, I'm trying to communicate an Experion C200 with SLC 5/02 and 5/03 controllers located on a DH485 network via a DHRIO module and a 1785-KA5...
Replies
0
Views
6,416
I am trying to set up point to point communications between a SLC 5/03 and a Panelview 600 touchscreen 2711-T6C5L1. I'm using the RS232 port on...
Replies
16
Views
12,093
I'm trying to write a data in Arduino using MODWR function block .I used the code I got from online for both PLC and Arduino. I made the wiring...
Replies
4
Views
119
Hello, I need to access the bits from the fire system control panel through RS-485. So, I used Read Var block to read from the panel...
Replies
0
Views
198
Back
Top Bottom