Hi guys, I've to connect some rs-485 component. My problem is that each device have a different connector type.
The breakers (Masterpact NT) (seven in fact) have screw connector, the second a Modicon 340 have a rj-45 connector and finally a Ge Versamax that get a db-9 connector.
I'm totaly lost. The master will be the GE.
Thks in advance.
I'd suggest that you consider breaking the DB9 wiring out to screw terminals, so that you can wire without spurs or stubs.
RS-485 is intended to be daisy chained, with incoming line on the same terminals as the outgoing line.
The incoming/outgoing line is not supposed to go to a terminal strip from which a separate pair of wires spurs or stubs off to the device.
By breaking out to screw terminals, you have flexibility for wiring that is awkward with DB9 connectors.
http://www.google.com/products/cata...ei=sffkTflqh7-BB-Wn8KIG&sqi=2&ved=0CFAQ8wIwAw#
I suspect the RJ-45 adapter with its transparent housing can be easily figured out because the wiring is in-line.
Which of the 9 pins in a DB9 are brought out to the 5 screw terminals is up for debate. Time for an ohmmeter . . . .
Hopefully it's the pins needed, because there is no standard or even convention for RS-485 in a DB9.
The cable that connects the DB9 on the device to the DB9 on the DIN rail adapter (above) is a stub or spur cabling. Stub/spur cabling creates reflections. That section of cabling/wiring needs to be minimized.
I am attempting to configure a new PLC network. So far my configuration is as follows: 6 x SLC 5/03 racks 6 x 1746-AIC isolated couplers 6 x PCs...
4,684
Is it possible for Modbus RTU and DH-485 to reside on the same physical network? I have a couple temperature controllers that can act as Modbus...
3,241
I have a customer using our Data Station Plus to collect data and do protocol conversion between a SLC (talking DH485) and a Modbus RTU device...
3,576
Good day all. I have an RS-485 topology question. I am hoping for some guidance so that I can make a confident calculation/decision that this will...
1,538
I have an allen Bradley system in which there is two micrologix 1200 and two panel view 300 and a Rsview 32 connected on DH485 network with the...
1,778