rslinks DF1 doesnt show panelview550
adx
Feb 2008
Dubai
i have rslinks 2.54 and panelview 550.i want to communicate both using serial cable 2711 NC13.but in rs links i can only see the workstation and not the panelview.when i lick auto configure in the rslinks DF1 driver it give message baut rate and parity not found.i keep baud rate 92000 and parity 1.please help me.
adx
PanelView 500 terminals can use many different protocols.
Post the full part number of your terminal, and a Forum member can tell you what RSLinx Classic driver and configuration are appropriate.
panelview not showing up in rslinks with serial cable
Hi Ken.my panelview terminal part number is
2711-K5A2 PV550 Key, FRN 4.10-4.xx
it is communicating with the plc with DH-485.
i have configured DF1 driver with parity 1 and baud rate 92000.when i browse in the rslinks i dont fine the panelview node.please help.
adx
adx
You need to use a DH485 driver, not DF1. You can't connect directly to that panelview with your PC comm port. Read the chapter on DH485 in the Panelview standard user manual.
What is your reason for connecting to the panelview?
If you just want to transfer programs, your simplest solution will be to use an ATA style memory card.
Paul
I think you may be able to connect using your cable and configure the 1747 pic/aic driver from linx. Then go to your panelbuilder software and click the pic/aic driver and you should see your panelview. This will give you the option to upload and download to the panelview. Let us know how you get on.
Another things is if you are configuring a 1741 pic/aic driver from linxs, you have to use a real serial port. It will not work on a USB to Serial. It will also not configure properly if you computer is running Windows XP SP3. Just wanted to give you a heads up on things to check if you have problems with the pic/aic driver.
Hello, I need to upgrade an old XP Computer to Win 7 that is being used to program Mirologix 1400 PLCs using RSLogix 9.0 and RSLinks. After the...
2,102
i recently purchased studio 5000, it opens fine but the rslinks that downloaded with it won't do anything when I click on the icon. I am running...
3,271
In the application tab of RSView Studio ME, there is no "communication setup" under the RSLinks enterprise so I cannot configure the...
1,129
I have a SLC 5/04 connected trough CH0 with a 2711-nc cable to a PV 550-b5a5. I can not auto configure the RSLinks to 5/04 CH0 using a 1747-CP3...
17
4,815
Hello and thanks in advance I have never used the Ethernet option to communicate to a plc. When I try to configure it in rslinks it never works...