RSLinx Classic Subnet connection to PLC not showing

terry56

Member
Join Date
May 2010
Location
California
Posts
45
Guys,
I am having an issue seeing a PLC through RSLINX.
In the image below, My PLC at 192.168.10.10 is connected to another PLC via the ENBT in Slot#13.
I can see the Remote Ethernet card, but I cannot see anything else. There is a 1756-L83E PLC, Input and output cards on site.
 
Exactly where the highlight is, "A, Ethernet", right click and select Properties. You can add the device addresses on the other network.
 
Thanks, yes I can add further sub addresses but that is not my problem.


I cannot 'see' the PLC System at the "A, Ethernet" connection. It should have a list of at least 7 other modules, including another PLC.
 
RSLinx is confusing in this regard. The ENBT at the bottom of your screenshot is the ENBT in slot 13, not the remote one. It's showing you Slot13 ENBT > Ethernet > Slot 13 ENBT

Try adding your L83's IP Address like I described above.

edit:

capture-20200410-125529.png
 
Last edited:

Similar Topics

On rslinx classic I can change the subnet mask. At my plant I have 3 ip ranges (10.136.8.xxx through 10.136.10.xxx) with PLCS on them. In classic...
Replies
2
Views
2,481
Hi, I am working on a project, where I face a issue with respected to Network Dropout. The PLC is connected to a 16 port unmanaged switch, where...
Replies
7
Views
193
Hey All, I am sorry to ask this, but i still gotta do it. What happens if I close RS linx? Will it cause network interruption and PLCs will lose...
Replies
5
Views
161
Does anyone know if there is a way to import RSLinx Classic data into FT Linx? We have a quite extensive configuration set up, and it would be...
Replies
8
Views
2,591
Hello, I entered my controller IP address as 192.168.1.100 (Local) for 1769-L33ER. It worked fine until couple month and found the controller kept...
Replies
1
Views
1,138
Back
Top Bottom