RSlinx - Copy DDE/OPC link

Here are some screenshots..

Topic_configuration.JPG


Copy_Link.JPG


Excel_SS.JPG
 
Its been a long time since I did this with a slc. The only two differences that I see is that I had tag name as "n7:0" I dont remember l1,c1. also I remember having problems with that lock before I got it to work also. probably not much help for you
 
WAQ, are you running RS security software. My software has the security stuff greyed out so I don't know how you get the lock symbol.
 
From your screenprint it looks like double quotes around the N7:0 - it should be single quotes.


=RSLINX|TESTSOL!'N7:0,L1,C1'


Mike
 
joesullivan8: How do I configure the windows "DDESHARE" for rslinx?

doug2: I changed it to just N7:0, it is showing the same value.

Mickey: I don't believe I have the RS security running. How do I verify that?

croakus: Those are single quotes..

Thanks for all your replies.. I appreciate..
 
Cryogen said:
joesullivan8: How do I configure the windows "DDESHARE" for rslinx?

doug2: I changed it to just N7:0, it is showing the same value.

Mickey: I don't believe I have the RS security running. How do I verify that?

croakus: Those are single quotes..

Thanks for all your replies.. I appreciate..

I don't know, I have never used that software.
I'm just wandering where that lock symbol comes from.
 
I believe you need to setup the windows ddeshare and tust it.
Start\run\ddeshare
make a *|* (generic share)
also go to services under admin and be sure your DDE services is enabled and running
Picture of ddeshare attached
 
Kidblue said:
Can you see the device in the browser window when you click the topic from within Linx? Just wondering if the Topic is still correctly associated with the relevant processor.....


Did you 'Paste Special' or just plain old 'Paste' in Excel?



Rob.
Hi Rob it's shaun vernon, from the Castings ,how's things.
 
Mickey said:
I don't know, I have never used that software.
I'm just wandering where that lock symbol comes from.

Any time I have an active item being serviced, I get the lock symbol too. I think it's normal. I am not using the security features of RSLinx either...
 
Problem solved!!

I am able to view the correct data now. I made two changes
- Created a windows DDE share (thanks joesullivan8 and RSlinx help topic)
- Checked the polled data collection mode (see pic), it was unchecked before.

RsLinxTopic1.JPG


Thanks for all your help..
 
Last edited:
OkiePC said:
Any time I have an active item being serviced, I get the lock symbol too. I think it's normal. I am not using the security features of RSLinx either...

Yes now I see it. I guess I never when back to RSLinx to look.
Thanks

Cryogen,
Thanks for getting back to us with the solution.
 

Similar Topics

Running redundancy for OPC topics (RSLinx Pro is the data server)...switched from primary to secondary so that I could add topics to the primary...
Replies
0
Views
1,485
I came across a process recently that is using rslinx pro for a RsView32 runtime PC. The strange thing is that the rslinx serial number is...
Replies
4
Views
14,754
Hi, I am working on a project, where I face a issue with respected to Network Dropout. The PLC is connected to a 16 port unmanaged switch, where...
Replies
7
Views
195
Does Rockwell still offer reset codes for old school Master Disk floppy's? In a bind and need to reset the activation disk soon and to be pointed...
Replies
9
Views
230
Anyone have issues with RSLinx being very slow to open. It sometimes will say "Checking Activation" at the bottom for what seems like an...
Replies
2
Views
158
Back
Top Bottom