Hi Everyone...
I am running FactoryTalk View SE Version 7.0 Distributed on a Primary and Secondary Server.
The issue I am having is that it looks like the RSLinx Classic OPC Topics are running on the secondary server but not the Primary.
When I reboot the secondary server, I get wire frames with the OPC Topic PLC 5s.
All the RSLinx Enterprise PLC's continue to communicate normally.
When the secondary server comes back online everything goes back to normal.
I have checked both RSLinx Classic settings on both servers and everything looks the same....
Any other settings I should look at???
If you Right Click on your Project Name and Select Server Status, what does it show?
Stu....
Are the topics mapped on both the primary AND secondary?
If it's running on the secondary - restart RSLinx service on primary.
Verify all your topics?
Check the FTLD Test Client to see if tags are resolving...
The Server Status shows the Primary as Active and the Secondary on Standby
Also,
I double checked the OPC topics on both servers and they are the same.
What is the FTLD Test client?
It is the Factory Talk Live Data Test Client. You will find it under Rockwell Software --> FactoryTalk Tools.
Stu....
We use RSLinx to interface a program which takes specific data from our PLC5 and applies it to specific fields on our enterprise software. We do...
1,783
Hi all, I have a question about OPC topic of Rockwell RSlinx, we use opc client in HMI to read the data in controllogix via Rslinx OPC topic...
6,211
G'day there, I want to send real time data to a VB6 application. It works in excel thanks to a previous response from member - plastic, but I...
3,811
I've already setup DDE/OPC topic at RSLINX OEM version. I even copied the link to excel. Now I saved excel file into our company's network drive...
3,351
Is there any mode to save the list of topic opc made with rslinx? regards
3,336