Hey Guys!! I'm new at learning how to use the Rslogix 500 program. Ive tried to learn a lot of this on my own. I have a question that hopefully you guys can answer!! Whenever I configure driver, I use Ethernet devices 9 (I'm using an Ethernet cable that comes out of my laptop to the processor). Without going around in circles, I click on the icon of the plc and an error 0x10 comes up. I know what it means but don't know how to fix. Any thoughts would be great Thanks!!

Nick Montague
 
According to tech support that error will come up when using a 1761-NET-ENI to connect to a SLC 5/03 or 5/04 but not with an Ethernet SLC. If you are using a ENI then they suggest the following:


  • RSLinx Classic v2.30 or later needs to be used,
  • Channel 0 of SLC-500 controller must be configured for DF1 full duplex
  • Pass-Thru bits in the controller: S34/0 and S34/5 must be set to 0.
  • Use Ethernet devices driver (AB-ETH) instead of Ethernet/IP driver (AB-ETHIP).
 

Similar Topics

I'm getting an Error code on my MSG instruction that I can't clear. The Error Code Number is d0. Description "No IP configured for the Network"...
Replies
0
Views
868
Well this one has me befuddled :banghead: I'm trying to install RSLogix Version 11 on a VMware with Windows 7. I've already got FTV ME 9.0...
Replies
12
Views
4,215
When using 4 to 20mA I have been using 3277 to 16384 for the input min and max. We had new controls put in for a machine several years ago and...
Replies
6
Views
1,651
Greetings i have a PLC station SLC 5/03 i do upload the application program from it and able to go online with the CPU . when i do any...
Replies
3
Views
2,216
Hi I need help solving this Fault Code 20h (Math Overflow Trap S5:0). I download the code into the ML 1400 PLC. When choosing RUN it gives me a...
Replies
22
Views
17,282
Back
Top Bottom