I'm Having trouble using the HSC Instruction. whan i try to enter HSC pop up box appers "HSC Instruction not supported by the current processor"???
What other instruction can I use in order to count pulse, since I cant use the HSC instruction.???
Thanks for you help
 
The modular SLC-500 high-speed counter modules (1746-HSCE, 1746-HSCE2) do not use the HSC instructions.

HSC instructions are specific to the embedded high speed counter subsystems in MicroLogix family controllers.

To start using the 1746-HSCE or 1746-HSCE2, begin with the User Manual and Knowledgebase documents giving example configurations.
 