RSLogix 500 Math Overflow Trap S5:0
harleymc100
Jan 2014
london
21
PLC errorrr.jpgHi Gurus
I have an issue with 2 similar programs. One faults and the other doesnt.
When i enter a number on the HMI larger than 546 ( MUL x 60 = 32760),
Program 1 faults (math overflow) but the other doesnt, and seems to max out the 32000 number to prevent a fault.
Is there a tick box im missing?
My logic basically is a blower that runs an on / off cycle. 999 minutes on and 1 minute off. Is there a better way to do this?
The largest integer number that an SLC-500 can handle is 32,767 so it correctly sets the Overflow flag when it multiplies a number greater than 546 by 60.
Can you provide more details on the program that doesn't seem to fault ?
One possibility is that you can account for/ deal with the Overflow by setting the Overflow status bit (S:0/5) to False with an OTU instruction before the end of the program.
Your program that doesn't fault the SLC might have that instruction in it. Some programmers do it as a matter of course, but I argue against that because it can conceal unintended consequences of the overflow condition.
Ken, you're absolutely right.
OTU S:5/0
This was in the "non faulting program" - Thanks so much. This is such a great resource.
So for future reference/learning. What is the "correct" way to address this issue? If for example, i wanted the drive on for 999 minutes and off for 1 minute. Series a few timers?
TIm
TIm
yes, divide HMI input by 2 and multiply by 60 and move value into 2 timer presets. When Timer 1 done then start Timer 2 when Timer 2 done then HMI Preset value has been met.
Hi my problem may have a simple solution but i cant work it out. I need to use the Divide function but it wont let me use a decimal point in...
1,745
Hi I need help solving this Fault Code 20h (Math Overflow Trap S5:0). I download the code into the ML 1400 PLC. When choosing RUN it gives me a...
22
17,242
I am trying to use the CPT instruction and apparently I can't quit get it right. I am trying to accomplish this equation. (( N25:4 * 1000 ) +...
2,923
Hello everybody I'm new to plc programming and i'm trying to program some simple math operations to convert some measurments for a project. The...
5,597
Hi Everyone, I am not proficient in RSLogix 500 so I have a question regarding the evaluation of N7:0 data as an input. So as I understand in...
87