harleymc100
Member
Hi Gurus
I have an issue with 2 similar programs. One faults and the other doesnt.
When i enter a number on the HMI larger than 546 ( MUL x 60 = 32760),
Program 1 faults (math overflow) but the other doesnt, and seems to max out the 32000 number to prevent a fault.
Is there a tick box im missing?
My logic basically is a blower that runs an on / off cycle. 999 minutes on and 1 minute off. Is there a better way to do this?
I have an issue with 2 similar programs. One faults and the other doesnt.
When i enter a number on the HMI larger than 546 ( MUL x 60 = 32760),
Program 1 faults (math overflow) but the other doesnt, and seems to max out the 32000 number to prevent a fault.
Is there a tick box im missing?
My logic basically is a blower that runs an on / off cycle. 999 minutes on and 1 minute off. Is there a better way to do this?