RSLogix 500 Pro Version 12

Galaxia_PLC

Member
Join Date
Sep 2019
Location
Ohio
Posts
2
Hello All...

I am programming a Micrologix 1400 series C and cannot "Save" online edits.

I can perform online edits, but when I try and save them I eventually get a warning: "You must configure the communications through the system comms dialog when using security".

I try and upload using the "System Comms" drop down and selecting the processor, but still the same message.

I am not even using security as far as I know.
Ladder properties have "Allow online edits" checked.
Controller properties does not contain Series C as a choice, only series A & B.

Any ideas?

Thanks!
 
I figured out something. In the past when I work with Micrologix controllers I always Automatically Configure the driver and it works. This time I noticed the Error Checking was BCC so I changed it to CRC and now I can save my online edits.

Thanks
 

Similar Topics

Hi, I’m looking at the difference between standard and pro versions of RSLogix 500. I know the pro version lets you edit the database in excel...
Replies
11
Views
2,755
So once again i am trying to create a program in unity pro from an Ab program. i have an FFL and FFU in rslogix 500 and need to use something like...
Replies
2
Views
2,219
1.the black switch is master start/stop switch 2. When red pushbutton is pressed once, both motor 1 and 2 should run continuously 3.if you close...
Replies
3
Views
1,753
Is there a "BOLD" font that can be used in the ladder logic of RSLogix 500 pro? The regular font drives me nuts.:banghead: TIA LW-c
Replies
2
Views
1,899
Not sure if this is the right place to post this, but wanted to see if this software was still worth anything to anyone. My father recently...
Replies
1
Views
3,600
Back
Top Bottom