First time using scale function and not quite sure whether it is right or wrong. Please advise and below is what I have
1. Using Allen Bradley 1766-L32AWAA
2. Temperature Transmitter is Prosense TTD-20-N40160F-H
3. PT100 is Prosense RTD0100-10-010-H
4. Write a simple Scale function. Input number is changing but I see no change on the output number
Please let me know why or what I should do to make sure I do it right.
Thank you!
nHIsq
Since I am new to this scale function, if someone can provide me some simple quote and method of testing, I would very appreciate that.
Then I can move to next step where I need to do some control according to the temperature change.
Hi Mike,
Since I am testing on this scale function, I wrote this in ladder file 17 and plan to use it later in my main when writing the some lesser than or greater than function to control my output.
Is that because I do not write any JSR in my main and it cause the output file got no number change when the input number is changing?
You guy are awesome!
After adding some simple command in my main, now I saw the changing on the output. I know I am in the right path now and continue working on the temperature control part.
By the way, I have a simple question to ask. Here is what I found when I doing the wiring connection
1. without a resistor between analog output and analog com, the result seem not correct
2. with a resistor between analog output and analog com, the result seem right
I will do the #1 method. Can someone tell me whether I am making the right choice and tell me why?
Thank you!
Most likely your sensor is a 4-20mA type sensor. The analog input on the Micrologix PLC's is a 0-10V analog input. If you put a 500ohm resistor across the analog input, then your 4-20mA will flow through the resistor, and ohms law will tell you that you now have 2-10V across the analog input.
So, without the resistor, you have a 4-20mA signal and a 0-10V input. This won't work. By putting the resistor there, you convert the 4-20mA signal to a 2-10V signal, and this will work on your 0-10V input.
Thanks for the detailed explanation.
Does it matter if I am not using 500 ohm? Is it critical if not using exact 500 ohm?
I only have 470 ohm or 680 ohm. Unless I solder it and put them in series.
Yes,
AB says that you need a 500 +/- 0.25 ohm resistor.
if you don't have one, the closer to 500, the better results you get.
you will also need to scale the input for best results.
We bought several from our electronics dealer and we use them for calibration and other things.
james
It doesn't matter if you account for it in the scaling. It's simple ohms law: V=IR.
Lets say you have a 470ohm resistor. We need to know the voltage at 4mA and 20mA.
For 4mA:
V=I*R
V=0.004*470
V=1.88
For 20mA:
V=I*R
V=0.020*470
V=9.4
So if you use a 470 ohm resistor, your 4-20mA will become 1.88-9.4V. This is within the range of the 0-10V input, so it will work just fine - you will just have to work out what values 1.88V and 9.4V correspond to on your analog input so that you can scale correctly.
If you were to use the 680ohm resistor, your 20mA would calculate out to be 13.6V which is above the measurable range of the analog input, so that will not work.
Long story short; use as close to 500ohms as possible, but if you must vary, go lower rather than higher and calculate accordingly.
Thanks for the suggestion, James.
Thank you, ASF for the detailed information with the calculation.
Conclusion, it needs in the range of 0-10V.
No it does not, you could use a 250 ohm giving you 1 to 5 v.
You will just lose some resolution with a smaller resistor.
Also keep in mind if you are using the embedded analog inputs the raw data
is 0-4095 for an input of 0-10v.
For 4mA:
V=I*R
V=0.004*470
V=1.88
For 20mA:
V=I*R
V=0.020*470
V=9.4
Using ASF's example..
1.88 v = 770 raw data value
9.4v = 3849 raw data value
Hi Everyone, I am not proficient in RSLogix 500 so I have a question regarding the evaluation of N7:0 data as an input. So as I understand in...
104
I have a little bit of experience with Allen-Bradley. I have a Micrologix 1500 (RSLogix 500) and a PanelView Plus 7 (FactoryTalk View Studio ME)...
198
buen dia. tengo una falla al pasar los tags de mi plc SLC 5 0/4 a mi panel me aparece un error Problem writing value " " to item <tag name>...
97
Will someone please convert this logic to pdf?
142
Hello, Haven't been on in a while. I need to generate a bit level pdf of the I/O for RSLogix 500. I can generate a report but it just shows the...
173