RSLogix 500 Scale Function Test
Thank you, Mickey for the further explanation.
May I know how to figure out the raw data value related with the voltage and resistor that have been chosen.
These raw data value will be the input min and max, right?
May I know how you come out with the value of raw date value.
Is these the value for the input min and input max?
As stated above the raw data for 0-10v input for the embedded analog input for the ML1400 is 0-4095.
1.88/10=.188
.188*4095=770
9.4/10=.94
.94*4095=3849
So using the "SCP" instruction and assuming the value of your resistor is exactly 470 ohms, then
Input min=770
Input Max=3849