hahaliao Member OP H Join Date Feb 2017 Location California Posts 12 Feb 23, 2017 #16 Thank you, Mickey for the further explanation. May I know how to figure out the raw data value related with the voltage and resistor that have been chosen. These raw data value will be the input min and max, right?
James Mcquade Member J Join Date Oct 2007 Location Nashville, Tennessee area Posts 3,686 Feb 23, 2017 #17 If you use the 470 ohm resistor, measure the resistance first so you have the exact value. then make your calculations. james
hahaliao Member OP H Join Date Feb 2017 Location California Posts 12 Feb 23, 2017 #18 Thank you, Mickey for the further explanation. May I know how you come out with the value of raw date value. Is these the value for the input min and input max?
Mickey Lifetime Supporting Member Join Date May 2003 Location Palmdale,Ca Posts 10,659 Feb 23, 2017 #19 hahaliao said: Thank you, Mickey for the further explanation. May I know how you come out with the value of raw date value. Is these the value for the input min and input max? Click to expand... As stated above the raw data for 0-10v input for the embedded analog input for the ML1400 is 0-4095. 1.88/10=.188 .188*4095=770 9.4/10=.94 .94*4095=3849 So using the "SCP" instruction and assuming the value of your resistor is exactly 470 ohms, then Input min=770 Input Max=3849 Last edited: Feb 23, 2017