Has anyone experienced the following issue on RSLogix5000 (currently on V16)



I have a PLC program that has been running on a site for a number of years; yesterday we logged in for some maintenance.


All of the Descriptions in the Controller tags are out of order and no longer match up to the points they are connected to.


The last modification on this system was changing the default time on a timer from 3seconds to 5seconds.
 
Sounds like something that could happen during a DB dump, unintentional(?) modification and re-load of the DB.

Do you have an older copy of the program that you can check in offline mode to see if it's also corrupted?
 
Yeah I have an old version that looks good (off-line at least), I'm thinking I will have to do a re-download of the code the fix it... never fun on a live system.



Not sure how this has happened as last time I was over everything was good, I do remember as I disconnected it asked if I wanted to sync the initialization values. Think I clicked no.
 
If it is just the comments/descriptions that are 'out of order', you can export the tags/comments from the good offline file, and import them while online. Just set tags to create new and preserve existing, and comments to import new and overwrite existing.
 
Thanks for the info!
I will attempt to carry out an import. Im assuming by doing this while online the changes will be seemless.

I hope to carry this out without any impact to the current system state.
 
I've seen this when a SLC program was uploaded using as offline file and uploading current config.


There was a rung added or deleted between and RSLogix says that comment was on Ladder 2 Rung 15 and puts that comment on that rung even though the proper rung is now 16 - and every comment after is off too. Then it gets worse if another rung was added later in the ladder.


My thought is sometime a tag was added before an upload that is causing all the descriptions to move up one.
 

Similar Topics

OK, I apologize up front for having to ask about this. I am still learning to deal with the transition from Logix 500 to 5000. There is no module...
Replies
33
Views
77,288
Hi folks, in the alarm manager of Rslogix 5000, the tag-based alarm has been created. But when I tried to change the condition, it was found the...
Replies
2
Views
156
I am completely stuck on building a ladder program that requires a start button to be pressed 3 times to turn on motor 1. Then motor 2 starts...
Replies
20
Views
577
First off, I'm a hobbyist-level programmer, and this program isn't controlling anything anything that could even remotely be considered "life...
Replies
18
Views
517
Back
Top Bottom