I do not have either PLC or PanelView Plus to test this. Let say I have tag in PLC program Machine_Bit. And I have tag HMI_Bit, which is alias to the tag Machine_Bit. In PanelView Plus application indicator connected to tag HMI_Bit.
My question: will indicator change its state when tag Machine_Bit is changing? It appears it will. However I was reading somewhere that it maybe not. I do not have any hardware handy to test this. Maybe someone can test and let me know.
Thank you,
PaulB.
Albertabound's answer is not really correct.
A tag in the the ControlLogix database is a tag.
Sometimes these tags contain data (i.e. a base tag), and sometime they don't (i.e. an alias tag).
Most importantly ALIAS TAGS DO NOT STORE DATA, they redirect tag access to the base tag. Data is only stored once
So, an HMI, addressing an alias tag, gets data from the base tag anyway, no difference
I don't see the source of data as relevant to the question.
Isn't this what you asked.....
... my post explained that there is only one place where the data resides, so your HMI addressing the alias tag, or the base tag, will make no difference.
So here it is... I just recently started thinking about when and why to use alias tags in RSLogix 5000. It is my understanding that an alias tag...
28
15,532
I have a project I am re-doing and would like to clean up the I/O tree by removing some un-used modules. I know in order to delete them I need to...
4,325
I am currently working on a project where IO is not being used but previously was used in the field. In logix for example I have a tag where we...
6,996
Why do we create Alias tags? For example "PIT_190_I" for an input. Can't you just use "PIT_190" for the input and logic? What is the benefits to...
42
30,469
Hi all, I'm working on my first RSLogix 5000 program. Thanks to the help of some of you guys I am taking advantage of the AOIs (add on...
18,655