RSLogix 5000 and ControlNet
naidanac
Feb 2016
Canada
Hello, everyone.
I hope you're having a good day.
I am currently working on an upgrade project for a client that has a dozen PLCs in a ring configuration on ControlNet.
I have the .acd files (RSLogix 5000 version 8) sent by the client, but I converted them to version 13 as that is what the latest Logix allows me to do.
With the conversion, I can see the produced tags, but not the consumed tags.
Am I missing something during the conversion?
I added the .xc ControlNet file to the configuration inside Logix, but it does not populate the I/O tree showing the other nodes.
Basically, I just need the I/O mapping of the producer and consumer tags between the PLCs.
I appreciate any and all your help!
Nevermind - I figured it out.
The controller model that was in the BOM was wrong - I selected the correct one and it populated correctly.
Thank you!
Hi all, I'm integrating a system deployed ten years ago into our plant's network for the purposes of management and recording its history...
3,334
Hello, After a little help. We have ControlNet set up in redundancy - how do i show which channel is active in the PLC code? Can see all the info...
3,984
I have 4 PLC racks. Rack 1 = PLC1 (1756-L1), Control Net 1756-CNBR, & Redundancy Module 1757-SRC Rack 2 = PLC2 (1756-L1), Control Net 1756-CNBR...
13,843
Hi folks, in the alarm manager of Rslogix 5000, the tag-based alarm has been created. But when I tried to change the condition, it was found the...
158