Hello, I'm currently working on a program that requires a PID instruction to keep the level at a set point.
Hardware:
Solenoid valve (Relay output)
Control Valve ( Analog 4-20 mA output)
ultrasonic Sensor ( Analog 4- 20 mA input)
Differential Level Meter (Analog 4-20 mA input)
Flow meter ( Analog 4 - 20 mA input)
VFD ( connected to digital output and connected to analog output for a 4-20 mA speed reference)
PLC processor 1769-L32E with Digital I/O - 1769-IQ6XOW4, Analog I/O - 1769-IF4XOF21 and Relay Output - 1769-OW16.
I already configured my I/O on Rslogix 5000 but i am confused on how to start to write this program. Any ideas how?
First at all, you need a philosophy of operation. So:
a) Ask for that document to your boss/client/production guy.
b) If the document does not exist, take paper and pencil and start writing it.
When the document will be ready you can start writing a program.
And welcome to the forum.
Similar Topics
Hello, I am trying to choose from 4 different tank levels (REAL) and choose the greatest number (highest) and set that to open that tanks valve...
Replies
7
Views
1,884
Hello, I am trying to read a barcode scanner input using a cognex dataman 280 barcode reader, store it another string, the compare with another...
Replies
1
Views
49
Hi folks, in the alarm manager of Rslogix 5000, the tag-based alarm has been created. But when I tried to change the condition, it was found the...
Replies
2
Views
166
I am completely stuck on building a ladder program that requires a start button to be pressed 3 times to turn on motor 1. Then motor 2 starts...
Replies
20
Views
603
Back
Top Bottom