RSLogix 5000 Unable to open logic.

micky

Lifetime Supporting Member
Join Date
Aug 2003
Location
DeRidder, La
Posts
83
Uploaded this project from a PLC that we need to make changes to. I am trying to figure out the reason I am unable to open the actual logic. Do I have the wrong revision or version of RS5000 or is there some sort of protection that is preventing me from opening them? Or did I just not pay attention and uploading the program incorrectly?

2023-03-02 08_34_37-RSLogix 5000 [1769-L35E 19.11].png
 
What's the error message? For example, I don't have structured text or function block languages installed on this laptop, and it will give an error message in that regard. "Failed to open routine - editor is not installed." in the very bottom left of the application.
 
The way those routines are grayed out makes me think there is Source Protection. Right-click one of them, open the 'Properties' box and see if at the bottom it says "Logic: Source Not Available"

If so, you won't be able to access it without the Source Keys from whoever programmed it.
 
The way those routines are grayed out makes me think there is Source Protection. Right-click one of them, open the 'Properties' box and see if at the bottom it says "Logic: Source Not Available"

If so, you won't be able to access it without the Source Keys from whoever programmed it.


This is my vote. Mini is not the issue.
 
The way those routines are grayed out makes me think there is Source Protection. Right-click one of them, open the 'Properties' box and see if at the bottom it says "Logic: Source Not Available"

If so, you won't be able to access it without the Source Keys from whoever programmed it.

This is my vote. Mini is not the issue.

If I was a betting man I would bet source protection as well.

Source protection it is

2023-03-02 09_57_08-RSLogix 5000.png
 
Call the OEM and see if they will release the logic

That's my next route.

Though judging by the names the customer called the OEM, I may be putting in a new PLC for the handful of IO that is being added...lol...drama
 
Last edited:

Similar Topics

for some reason when i try to change the value for the preset on a rto timer after i change it accept changes it goes back to the old value, any...
Replies
4
Views
2,189
We got a new computer, and software a few mothes ago and have had plenty o' trouble with them. I know I should be able to edit online with...
Replies
23
Views
52,354
Hi folks, in the alarm manager of Rslogix 5000, the tag-based alarm has been created. But when I tried to change the condition, it was found the...
Replies
2
Views
158
I am completely stuck on building a ladder program that requires a start button to be pressed 3 times to turn on motor 1. Then motor 2 starts...
Replies
20
Views
586
Back
Top Bottom