RSLogix - MSG communication with no Ethernet/IP device

JohanM

Member
Join Date
Sep 2015
Location
Terchová
Posts
53
Hi guys. Do you have some experience with creating connection and read data from classic Ethernet device? I have to establish communication between CompactLogix with Ethernet/IP ports and SOLARTRON Orbit3 ETHIM module. I know his IP addresses, I have to send that what is on attached picture, but I dont know what select in MSG configuration 🔨

Bez názvu.jpg
 
You have to use Logix Socket interface
See Rockwell technote 32962 to learn how to do it.

Please note that older CompactLogix don't support Sockets.
 
You have to use Logix Socket interface
See Rockwell technote 32962 to learn how to do it.

Please note that older CompactLogix don't support Sockets.

Hi Contr_Conn. I found that manual before and now communication works, with some little problems. But when I will make it work like a charm I will add guide here for this specific case.
 

Similar Topics

I'm trying get information from another same PLC PLC1: CompactLogix 1769-L16ER-BB1B (192.168.0.133) PLC1: CompactLogix 1769-L16ER-BB1B...
Replies
17
Views
1,610
I'm getting an Error code on my MSG instruction that I can't clear. The Error Code Number is d0. Description "No IP configured for the Network"...
Replies
0
Views
870
Hello everyone, it is the first time that I need to exchange messages between 2 PLCs, a L16ER-BB1B and an L61. The first has 192.168.1.1 as its...
Replies
15
Views
4,473
Hello, I was curious if any one could shed some light on setting up a MSG statement between two PLC's on different networks. I'm trying to read...
Replies
1
Views
1,331
If you click help and then click Vendor Sample Projects while in RSLogix 5000, a PDF will pop up with some neat examples. One example shows how to...
Replies
5
Views
3,872
Back
Top Bottom