Rslogix5000 PID oscillating between 0 and 100 percent
p_logix
Aug 2008
winnetka
52
Hello all,
I cant figure out why my PID is oscillating between 0 and 100 percent. My set point is steady and whenever I take my PID out of software manual and put it in auto my CV jumps from 0 to 100 percent. We had a problem where a bus bar blew up and caused our network to go down. The program and gains have not changed.
Any ideas?
-Thanks
I got it. I had to set the output limit high to 99% the back to 100 %. And the PID took off. I found a technote through RA KB.
Hello all,
Any ideas?
-Thanks
You aren't clear.
You have it in manual at 0, then put it in Auto and it swings from 0 to 100 and then back to 0, or just go from 0 to 100? If it swings back and forth, try reducing your P and I gains by half until it quits swinging.
You aren't clear.
PV was steady and so was the set point. The controller turns into bang-bang control.
I figured it out. It was swinging back and forth 0 to 100%. It is actually a software problem with Rockwell PIDs. The work around fix is to make a small change to the output limit high hit apply then put it back to the original setting hit apply then the PID starts working. So I went from 100% to 99.99999% then back to 100% while in software manual. After putting it back in auto the PID controller wakes up and starts working.
Hello, I have a program that monitors pressure in a manifold discharge pipe. Pressure in the pipe should be less then 7.5 PSI. If the pressure is...
17
12,826
Hello, Question: (Temp is whats being controlled here by 3 fans) Using a PID; can I set my output (CV) to be 100% at a specific input (PV)? In...
2,267
Hello, I have already searched for that in the forum but did not get any satisfying answer, so here it goes: I have a 1769-L36ERM that controls...
3,133
Dear all I would like to ask you for help in solving one algorithm, because I never worked with cascade PID. I have to realize heating valve...
8,375
Hi ! Here is my first post :) I want to implement three (3) independent PID controlers (block) in a Controllogix controller. They will be used...
2,061