RSNetWorkx

Aye Min Ko

Member
Join Date
Jun 2014
Location
Yangon
Posts
3
If some one know my problem , please help me.
Now i using RSLogix 5000(V19.01) and RSNetWorkx (V10.01).PLC is Compact Logix L31 , 1769-SDN and 1794-ADN.When I go online using RSNetWorkX, i found my device SDN and ADN.But they show with question mark.So i register using EDS Wizard, it complete without no error.After that i double click on SDN, it say again it is not register.Device picture inside RSNetworkx is only square box inside question mark.Not show the actual picture.I don't know how to solve.
With Best Regards,
Aye Min Ko
 
Have you installed any recent software for compatibility with Studio 5000 v21 ?

The EDS subsystem was changed for v21 and any of the associated software will break RSNetworx and the EDS registration process from earlier versions.

That includes Studio 5000 v21, RSLinx Classic 3.51 or 3.60, or FactoryTalk View 7.0.

This can be patched, but you will need some help from Rockwell Automation Technical Support to do so.

The problem might also be unrelated to that.

When you create a blank project and browse the network, do the devices show up as Unrecognized ?
 

Similar Topics

Hello, Please I need help 🤞🏻, I would like to establish the sending and reception of data between SLC500 Allen Bradley and DSP Texas...
Replies
5
Views
3,592
Hi, I am new to Devicenet and I am having some problems with the EDS files. I was browsing through AB knowledgebase and this forum for some...
Replies
2
Views
2,211
I have been tasked with verifying that a new ControlNet network is functional using RSNetworx. This is new territory for me, any suggestions or...
Replies
4
Views
3,592
Back
Top Bottom