Hi All
Is it possible to connect non AB Ethernet devices to a Compactlogix 1769-L35E, without the use of RSnetwork for Ethernet?
Thank you
RSNetworx for EtherNet/IP is principally a diagnostic tool, or used with specialty non-Logix controllers. It is not used when connecting a ControlLogix or CompactLogix to I/O devices.
Whether or not your "non-AB device" is easily interfaced with a CompactLogix depends on the Ethernet protocols it supports. Generally it needs to support the "EtherNet/IP" application protocol.
Thank You,
I will be trying to connect an ABB ACS355 VFD, through a ABB FENA11 Ethernet card to a Compactlogix 1769-L32E.
That should be no problem; the FENA-11 supports EtherNet/IP, ProfiNet, or Modbus/TCP depending on a parameter setting in the drive.
I haven't used them for quite a few years so I would have used the "generic module object" rather than an "EDS-based Add On Profile" that might be available today.
But you definitely don't need RSNetworx for EtherNet/IP, just RSLogix 5000 software for the CompactLogix.
I am trying to test a motion control product and .eds file in RSNetworx for EtherNet/IP. I am using a CompactLogix L23E QB1B processor, firmware...
5,542
Hi guys, I'm currently working on a small project which has a 2 CPU compact logix running on Ethernet into a switch and 1 RSView SE server & 1...
3,871
Are there any real benefits or requirements to using RSNetworx for Ethernet/IP? We're gonna start up a new line in July, and prepare a...
7,289
I am getting random comm loss (error code 561 i think?) anyway i looked it up and its loss of comm to 2 modules on a controlnet network. The 2...
352
The back story: We have one customer that has some equipment that uses DeviceNet that must remain in place. On those (5) DeviceNet networks they...
897