hi,
how can be sure that if user program were lost during wrong precedure to replace backup battrey.the plc now showing only digital inputs ( LEDs in all input models are ON).
i made all kind of resets ( overall reset, reset,cold start,etc)
the machine control panel which is connected to the PLC tharough 9 pin connector indicates a communication error>
can i relaod the user program so that this communication error disapear.
regards
Hi abosaa
Do you have Step5 software and cable connect from PC to PLC? If you have, you connect to PLC and check the program inside PLC. But I think you was lost it because you made overall reset.
If you switched off the power supply module when the backup battery was changed then you can be certain that you have kissed goodbye to the program.
As TheVo states, if you have Step5 software, cable and a backup of the program, you can reload it and solve your problem.
Paul
TheVo said:
Hi abosaa
(Do you have Step5 software and cable connect from PC to PLC? If you have, you connect to PLC and check the program inside PLC. But I think you was lost it because you made overall reset.
hi. Mr.TheVo,
i have siemens PG and cable but it was supplied to 155H plc. can i used it for 115U?
if the plc shows the input leds only( all oupt modules were off) is that mean there is no user program?
regards
abosaa2001,
If you did a overall reset you have cleared the processor memory and there is no program inside now. I hope you have a backup copy of the program for the PLC.
You can use the PG and cable to connect to your 115 PLC. The 155 is just a higher end Siemens PLC.
If you need more info let me know. Am at work all night tonight and will be back in tommorow night.
Larry
I have recently started a new job and to my surprise the site has quite a few S5 plc's. I had the official training with siemens over 20 years ago...
2,336
Hello, I want to add an additional analog output module (8 A0 4...20 mA) to S5-115U in rack CR 700-3, but there are no free slots in CR 700-3...
1,899
Hi.. I have one problem with siemens S5 115u cpu 942B. In that cpu, EPROM module of 32kb is installed. Now, i changed one segment in the program...
4,092
Hi I am no siemens expert and have been asked to price for changing out an old obsolete HMI unit (it has a large keypad, lots of F keys and a 2...
7,935
We have a Siemens S5-115 944 which a couple of times a week faults out. All 4 red L.E.Ds on the processor are lit. The LEDs are identified as ST...
6,945