Siemens s5-115 fault
Potter
Nov 2004
Nottingham, England
77
We have a Siemens S5-115 944 which a couple of times a week faults out. All 4 red L.E.Ds on the processor are lit. The LEDs are identified as ST, QV, ZY and BA.
Reseting the CPU clears the fault and the machine runs ok again.
Any ideas what the LEDs mean or what could cause this?
115U CPU943/944
The LEDs are:
ST = stop mode
QV = I/O timeout
ZY = scan time exceeded
BA = outputs disabled
Is the stop LED steady, flashing or flickering?
Have you output the ISTACK and analysed it?
The stop LED is steady.
Not sure what you mean by "Have you output the ISTACK and analysed it?"
Problem is I'm not familiar with Siemens. I'm pretty new to this company. Lot's of experience with AB and Mitsubishi, but not S5.
Hello potter;
You should start by opening the Siemens support website (www4.ad.siemens.de), go to Product Support, search for and download the CPU 944 manual:
6ES5 998-0UF23.pdf
Chapter 5 is all about diagnostics, using the LEDs and the interrupt stack (I-Stack). The I-stack is available through the Step5 programming software, in the online functions. An explanation of the cause of faults is also included in the manual, so you can see the origin of your problem.
This is an excerpt:
Hope this helps,
Daniel Chartier
I have recently started a new job and to my surprise the site has quite a few S5 plc's. I had the official training with siemens over 20 years ago...
2,334
Hello, I want to add an additional analog output module (8 A0 4...20 mA) to S5-115U in rack CR 700-3, but there are no free slots in CR 700-3...
1,899
Hi.. I have one problem with siemens S5 115u cpu 942B. In that cpu, EPROM module of 32kb is installed. Now, i changed one segment in the program...
4,092
Hi I am no siemens expert and have been asked to price for changing out an old obsolete HMI unit (it has a large keypad, lots of F keys and a 2...
7,935
hi, how can be sure that if user program were lost during wrong precedure to replace backup battrey.the plc now showing only digital inputs ( LEDs...
3,894