S5-155U and CPU948

dm_srini

Member
Join Date
Feb 2008
Location
AQABA
Posts
3
Iam new to siemens systems and trying to install S5-155U CC with a CPU 948 in a very old plant.The CPU is OK and RUN LED is Green and iam able to communicate with PG and write small programs. The moment i adress an IO, the ADF error LEd flashes. The adress swith in the module is checked. The CC has no IM modules and is a standalone system with one CPU and few IO modules. The location of the inderted modules is OK.

What else to be done to get rid of the ADF error. Iam trying to simulate inputs by giving voltage but no change in status.
Any IO assignment to be done? If so how? Please help.
 
Your I/Q modules needs voltage and also you need to enable them
via either connecting 24V to the F+ F- OR briding 1 and 2 on X20 ( is situated on top of the module ,about same place as the adressing dip switch)

hope it helps

Eric
 

Similar Topics

i have an old PLC : S5 155U (CPU 948) i need to connect it to ABB PLC using Profibus-DP, ABB will act as Master and S5 as slave. I need to...
Replies
3
Views
3,009
Hi! Everyone~ I want to know is there some way can copy program code from one cpu to another cpu, and append it? My system has two cpu948, A and...
Replies
5
Views
2,212
Hi~ I have a question about Intouch. this is,could Intouch directly read/write date(DD,DW,I,F...etc) from/to PLC via H1Server? assume all setup...
Replies
3
Views
2,387
Hi~Everyone,I don't understand what mean this code, need your guys help, Thanks!! I have two FX block(FX131 and FX132) ,they call the same...
Replies
8
Views
2,674
Hi~Everyone!! I have some question about datablock (DB)? 1.CPU how to exchange data via DB?? I have a two CPU in one Rack, one is PLC1-1 and the...
Replies
1
Views
1,732
Back
Top Bottom