I am using the internal 24Vdc to supply all of my inputs and outputs.
When I shunt L+ with 1L and 2L, all of my outputs go high! Why?
Also All the negatives sides of the inputs and outputs are connected to M. The outputs and inputs devices all together do not exceed the 400mA limit.
Do I have to use a separate DC supply for the outputs?
Does anyone have a wiring diagram that uses the internal power supply for all of the outputs and inputs? I have seen the system manual for S7-1200.
Thanks in advance,
Bruno
Solved my problem!
I inverted the positive with negative lead on the output devices: block of electropneumatic valves from Joucomatic.
Regards,
Bruno