necyil Member N Join Date Nov 2004 Location Turkey Posts 102 Jan 4, 2014 #1 Dear ALL, I comunicate mm400 with s7-1200. Send speed referance to micromaster. Drive running. But cant see actual speed. Monitoring SPEED=0. Need help you can see on attached. Thanks for all help nec
Dear ALL, I comunicate mm400 with s7-1200. Send speed referance to micromaster. Drive running. But cant see actual speed. Monitoring SPEED=0. Need help you can see on attached. Thanks for all help nec
necyil Member OP N Join Date Nov 2004 Location Turkey Posts 102 Jan 4, 2014 #2 any answere? possible PZD_LEN?
JRW Member Join Date Jun 2002 Location South Carolina Posts 2,304 Jan 8, 2014 #5 What's in P2019.1 of the MM4? Drive default is r21 (filtered Freq) If you fault the drive (cause an external fault) do you see the fault bit? (Status word) I'm assuming the uss control is working ok, because you said "drive running" Last edited: Jan 8, 2014
What's in P2019.1 of the MM4? Drive default is r21 (filtered Freq) If you fault the drive (cause an external fault) do you see the fault bit? (Status word) I'm assuming the uss control is working ok, because you said "drive running"
rgua Lifetime Supporting Member R Join Date Mar 2003 Posts 144 Jan 8, 2014 #6 Set P2012 = 2 (uss PZD length)
necyil Member OP N Join Date Nov 2004 Location Turkey Posts 102 Jan 10, 2014 #7 Hello Control are working and P2012=2.I cant see actual speed.
JRW Member Join Date Jun 2002 Location South Carolina Posts 2,304 Jan 10, 2014 #8 See post 5 What's your parameter ?
KalleOlsen Member K Join Date Oct 2008 Location Norway (moustache area) Posts 1,782 Jan 10, 2014 #9 necyil said: Hello Control are working and P2012=2.I cant see actual speed. Click to expand... You are not supposed to see the speed there, it is a parameter value to be set by yourself. Do you connect directly to the terminals of the IO board, or via a BOP? If you don't like time lasting quizes, please provide all the settings regarding USS in the MM. p700 p1000 p2009 index 0 p2009 index 1 p2010 p2011 p2012 p2013 p2014 and p2019.1 as JRW has asked for since long... And do you see any counting in r2024 r2025 PLEASE check it all! Kalle Last edited: Jan 10, 2014
necyil said: Hello Control are working and P2012=2.I cant see actual speed. Click to expand... You are not supposed to see the speed there, it is a parameter value to be set by yourself. Do you connect directly to the terminals of the IO board, or via a BOP? If you don't like time lasting quizes, please provide all the settings regarding USS in the MM. p700 p1000 p2009 index 0 p2009 index 1 p2010 p2011 p2012 p2013 p2014 and p2019.1 as JRW has asked for since long... And do you see any counting in r2024 r2025 PLEASE check it all! Kalle
necyil Member OP N Join Date Nov 2004 Location Turkey Posts 102 Jan 10, 2014 #10 Hello p700=5 p1000=5 p2009=0 p2010=4 p2011=3 p2012=2 p2013=127 p2014=0 p2019.1=21 (default) i need ideas thanks
Hello p700=5 p1000=5 p2009=0 p2010=4 p2011=3 p2012=2 p2013=127 p2014=0 p2019.1=21 (default) i need ideas thanks
KalleOlsen Member K Join Date Oct 2008 Location Norway (moustache area) Posts 1,782 Jan 10, 2014 #11 Thank you, what about counting in r2024 r2025 I wonder about the PKW setting of 127 (p2013). Is this described explicitly for the S71200 FBs? With Profibus DP the PKW length is 4 words. And also it is normal to run without PKW (0 words). Perhaps worth a try. Kalle Last edited: Jan 10, 2014
Thank you, what about counting in r2024 r2025 I wonder about the PKW setting of 127 (p2013). Is this described explicitly for the S71200 FBs? With Profibus DP the PKW length is 4 words. And also it is normal to run without PKW (0 words). Perhaps worth a try. Kalle