S7 1200 Processing of analog input (mA)
npalavras
Mar 2013
Greece
Hi to all,
I am newbie in PLC and I have a project to do with Siemens s7 1200.
I have one Analog Input, IW1 which is 4 – 20mA from a flow meter and I want to represent it on HMI as m3/h with scale 0 – 1000 m3/h .
When the flow falls below 50% (500 m3/h) an indicator ‘’low flow’’ must be on.
I make some steps which I am not sure if are going to work (see attachment) and I don’t have any idea how to continue it and represent on HMI.
Please for a help!!!
here it is, i made you also a hysteresis for analog input on low flow
PS: don't know how to resize the picture to small preview
I would like to thank you for fast reply.
I also would like to ask you:
· At your NORM X block the min is 0 and max 27648. As my signal is 4 – 20mA I suppose that the min value must be 5530(4 mA) am i wrong?
· At your capture sorry but I can’t see the hysteresis.
Well if you have a 4-20ma card then input sshould be 0. Or maybe 8 precisly dont know the exact tech specs of your card. 5537 is if you use internal 0-10v input.
As for hysteresis whaz you dont see is reset if tag_4 > 505.0 to avoid pulsation of analog value
in s7-1200 manual it said Whenever the operating mode changes from STOP to RUN, the CPU clears the process image inputs, initializes the process...
1,058
Hi all, Currently having trouble getting a speed reference to write over modbus to an Omron M1... I can successfully write a run command and...
257
HI i would like to know how to get a variable that will store the amount of times a program has been executed. The issue is I have 3 DBs for 1 FB...
82
Hi, I have attached herewith one image which our programmer has been used in S7 1500 PLC. Now we need to use the same instructions in S7 1200 PLC...
120
commentaire communiqué siemens s7-1200 avec vfd delta ? (cablage et sur tia portal )
139