S7 1200 to Sepam MODBUS RTU Addressing

boneless

Lifetime Supporting Member + Moderator
Join Date
Feb 2008
Location
OKC
Posts
1,628
Hi all!

So I got tasked with this fun little project. I have never done anything with MODBUS RTU and am having quite a bit of fun doing this. One little issue I am unsure about.

Schneider is delivering 2 SEPAM units that are supposed to communicate with our 1200 CPU (with CB1241 interface installed).

The Siemens program is set up to communicate with registers 40000 and up, while the IO table I got from Schneider references HEX codes 010B and up.

Am I right to assume that I can just add 010B to my 40000? FE 40267 in that case?

Thanks!
 
We got this working today, clue is just to add 40001 to the addresses provided.

So, for current. HEX 0113 = DEC 275. Is 40276 as input into the Siemens FB.

Whoop!
 
I have to say that the manual is very good actually, the problem is my lack of knowledge :).

They way Siemens (seems) to do function codes etc, is by adding a specific range to the address. Hence the 40001 added (function code 03).
 

Similar Topics

Hi all, Currently having trouble getting a speed reference to write over modbus to an Omron M1... I can successfully write a run command and...
Replies
6
Views
256
HI i would like to know how to get a variable that will store the amount of times a program has been executed. The issue is I have 3 DBs for 1 FB...
Replies
2
Views
82
Hi, I have attached herewith one image which our programmer has been used in S7 1500 PLC. Now we need to use the same instructions in S7 1200 PLC...
Replies
4
Views
120
commentaire communiqué siemens s7-1200 avec vfd delta ? (cablage et sur tia portal )
Replies
0
Views
135
Hi, I have a 1214 on ip 192.168.0.100. This is connected to other modules through a switch on same network. I need to connect this to a company...
Replies
1
Views
183
Back
Top Bottom