S7-1500F and S120 over Profisafe SLS
cottagewood
Oct 2005
Kent
179
Has any one got any experience with Safe Limited Speed , I've used the standard library functions for the drive safety and standard telegrams, LDrvSafe_SinaSTlg30Control,LDrvSafe_SinaSTlg30Status and telegram30.
The safety in the drive has extended safety functions and the safety is commissioned with no errors
when I make the SLS bit high in the PLC function block it doesn't activate it in the drive. All the other communication functions between the PLC and drive are working, including STO
How are you monitoring the SLS activation in the drive?
You turn the SLS bit to zero to activate it.
I'm trying to download a project for Siemens S7-1517F safety PLC to S7-PLCSIM Advanced 3.0 simulator and I'm getting incompatible firmware issue...
1,573
Is it possible to use the feed back safety function with a drive over profi-safe and if so, what do I use for the input QBAD_FIO? If I was doing...
1,933
Hello all, I am planning an application where I have a cluster of conveyor belts (~20) where each on has its own local E-stop. I want to use an...
2,645
Hi I need a safety system with safety encoders as input (profisafe bus) and digital outputs. When position or speed of some rotating device...
1,736
Hi all, I am having a machine with old 802d sl siemens controller. I am trying to tune servo by Siemens starter software. Anyone experienced...
69