S7 300 communication via cp343-1 lean

haithm

Member
Join Date
Feb 2021
Location
cairo
Posts
11
I can not see the CPU s7-300 i only see the cp343 as photo the interface is through tcp/ip how can I upload the station via the cp343 module ???
 
I forget photo , sorry
is it possible to upload the cpu program via cp343 module ?? As I can see cp343 online but the cpu 313c do not appear online
How can I do that ???

20210316_171441.jpg
 
You select Upload Station to PG.
You will get the dialog that you have posted.
Be sure to select Slot=2 instead of Slot=0.
You should now be able to upload.
 