I'm from an Allen-Bradley background and am having my first experience of Siemens. I have an S7-314 that I keep needing to manually cycle the Run/Stop switch to get it into run. Looking into the diagnostics I get the following error:
1 of 351;
Event ID: 16# 3842
Module OK
Module type: Distributed I/0s
Input address: 2042
Channel information available
Requested OB: Diagnostic interrupt OB (OB82)
OB not found, or disabled, or cannot be started in the in the current operating mode
7/15/1994 17:36:13.322
Can anyone guide me where to look to solve this? Thanks,
Ben
Exactly, put empty OB blocks mentioned above to PLC - it won't stop but still report the error.
The solution for keeping the plc in run is downloading ob82 but you have to look for the fault at your distributet I/O's address 2042. Maybe bad power connections/lov voltage, bad network or faulty hardware..
Jonas
OK guys, i've just been back to site and i'm getting the following error: Does this suggest and error with the profiNET connections?
6 of 377;
Event ID: 16# 39CB
PROFINET IO: station Failure
address of the affected station: Input address: 2042
IO system ID: 100
station number: 1
Log. Basic address of the IO controller: 2043
Requested OB: Rack failure OB (OB86)
Priority class: 26
7/17/1994 05:01:22.275
in allen bradley kinetix 300 drive first E31 error shows after resting drive E11 error occurs need solution to reset E11 fault code
147
123
284
Hi i using Kinetik 300 2097 driver control by EIP with using move absolute and incremental for motion , but i want to add same driver and motor as...
72
Hey all, first time poster here. I am wondering if anyone has tried using a Keyence SR-X300 barcode scanner to a Micrologix 1400. Keyence sent...
83