S7-300, MP377, Scalance S612 Time Synchronization

Hal9000

Member
Join Date
Jun 2010
Location
London
Posts
140
Does anyone have any examples or experience in time syncronizing their S7-300 PLC and MP3xx HMI with an NTP time server?

My set-up

External Network -> S612 Scalance (with NTP configured)-> Internal Network -> X-106 Switch -> S7-300 CPU 315-2 PN/DP
-> MP 377


I would like the PLC and HMI to pick up their time/date from the NTP server that is configured in my S612.

Any help in doing this would be greatly appriciated. The simpler the better.

Cheers.
 
Hi,
for HW config use this:
HW_Config.jpg.
You should enter the IP adress of the S612 device there.
For the HMI I know only how to syncronized with PLC(not direct from S612):
Conf_HMI.jpg,
when on db1.dbw 0 you should enter the adress when is the current time of the PLC readed with SFC1.And there should be some more bytes for system use
Regards,
Mitko
 

Similar Topics

Hi, I'm setting up a modbus master on an S7-300. It seems to work in OB1 but not when I use it in OB35. Does anyone have any ideas why? Could...
Replies
10
Views
114
So basically i have 2 queries : 1. I have a program file of S7-300 PLC which i want to migrate in RSLogix500.In short i want to convert my simatic...
Replies
15
Views
263
Hi i using Kinetik 300 2097 driver control by EIP with using move absolute and incremental for motion , but i want to add same driver and motor as...
Replies
0
Views
64
Hey all, first time poster here. I am wondering if anyone has tried using a Keyence SR-X300 barcode scanner to a Micrologix 1400. Keyence sent...
Replies
0
Views
64
Hi Siemens guys! I am experiencing SF fault on our S7-300 (6ES7 315-2AH14-0AB0) CPU from time to time. I've checked the diagnostic buffer and...
Replies
13
Views
195
Back
Top Bottom